The designation on each page is incorrect as IEEE Std C37.102-1006. Correct the designation in the headers on each page of the document as shown:
IEEE Std C37.102-2006
The text in 4.4.1.5 is incorrect. Correct the text to read as follows:
The relay set points are in ohms typically with a 20 kΩ alarm and 5 kΩ trip or critical alarm.